I understand the type of panel you refered too. My point is by installing this equipment using section 230.82 (2), the conductors leaving this panel would be considered “service conductors” not feeder conductors.
If this equipment were installed on a pole remote form the building being served; how would this relate to section 230.7 Other Conductors in Raceway or Cable? Using 230.82 (2) theoretically the service conductors down the pole to the meter and (not service) disconnect could occupy the same conduit as the service conductors going back up the pole that could serve a building with the service equipment.