Well you guys have helped me on the last generator questions so much. I could use your help on my other generator issues.

Heres the new story....

We have a residential home, with 2, 200A service sub panels. We will be installing a 35+Kw Genny, w/ an ATS.

The way I figured the install is... Out of the meter to the ATS, from the ATS to a Disconnect,.. At this point we need to split and go out to the 200a panels.

Sounds good to me... but..

The disconnect, where I can come in with that 400a and split it to the 2 , 200a panels. What is the best route to go here, a 4 space panel? Install two 200a breakers then out to the panel? I checked with the supply house they don't seem to be familuar with a disconnect specific for this application.

So... feel free to comment. [Linked Image] .. and thank you.