I will first have to go through a meter then to a fused disconnect.
That will be a problem.
240.21(B)(2)(2) The tap conductors terminate in a single circuit breaker or a single set of fuses that will limit the load to the ampacity of the tap conductors. This device shall be permitted to supply any number of additional overcurrent devices on its load side.
Bob Badger Construction & Maintenance Electrician Massachusetts