Calcs:
For minimum service: VA A (120)
3VA/sqf (existing) 4500 38
3VA/sqf (addition) 6000 50
1500A App Ckts (exst) 1 13
1500A App Ckts (new) 2 25
Water Heater 4500W 32
Range 40A 240 80
Dryer 28A 240 56
Subtotal: 35217 293
First 10k: 10000 83
40% of rest: 10087 84
New Subtotal: 20087 167
Furnace 60A 240 120
Furnace 60A 240 120
[b]Total: 48887 407
per phase: 24443 204[/b]
Here's the panel loadouts:
Old
150A Main Panel
Dryer 30 A/C 30
Dryer 30 A/C 30
Bedroom 15 Bedroom 20
Bedroom 15 Fridge 20
Lights 15 Kitchen 20
Liv Rm 15 Kitchen 20
Bedroom 15 Washer 20
Furnace 60 Water 30
Furnace 60 Water 30
Range 40
Range 40
PH-A 260 PH-B 295
Reconfigured
200A Main Panel
Dryer 30 A/C 30
Dryer 30 A/C 30
Bedroom 15 Bedroom 20
Bedroom 15
Lights 15
Liv Rm 15 Library 20
Bedroom 15 Washer 20
Furnace 60 Water 30
Furnace 60 Water 30
Feeder 100 Range 40
Feeder 100 Range 40
PH-A 340 PH-B 375
New:
125A
Furnace 60 A/C 30
Furnace 60 A/C 30
Lights 15 Bedroom 20
Lights 15 Sewing 20
Lights 15 Kitchen 20
Bath 20 Kitchen 20
Doors 15 Fridge 20
Shed 20 Garage 20
Shed 20 Dining 20
Micwv 15 Living 20
Outlets 20
PH-A 240 PH-B 255