Does the new requirement for "rain tight" EMT fittings require a gasket between the fitting and the enclosure?

The sites I looked up that UL says are listed for making rain tight fittings either have gaskets at the knock out or gaskets that are ordered seperately.

As a side note. I have been told NEMA 3R enclosures are allowed to have water leak into them as long as they don't cause a short. It seems to me that you would want to do your best to keep water from leaking into any exterior mounted enclosure. Especially when the conduit entry is directly exposed to the weather. In this case a rooftop in Brooklyn.

Robert

While I'm on a roll, does an insulated throat in a connector (EMT/LT/GF) serve the same purpose as a plastic bushing, or is a bushing still/always required?