The average temp in my area in the summer is about 90- 105. as per sec, 310.16 table, if the temp exceeds 86 F ,a correction factor is required, as to derate the ampacity of the conductors. most of the electricians in my area do not apply the rules of 310.16 and 310.15(2)b tables. do you apply the rules of derating ?