These are probably "back wired" receptacles that you are talking about. Look at them more closely. Do they have small holes next to the screws in the back? You insert the conductor(s) into the hole(s) in the back, and tighten the screw(s), which in turn tightens a pressure plate on the conductor. Side wrapping is not required.


Peter