Please consider grounding the 120V-secondary winding. For 1000VA-and-under control-power transformers, NEC 250-30 allows the winding to be grounded with a simple 'case' jumper. The usual full-tilt grounding-electrode/building-steel connection is not needed. This is a real easy way to keep electrostatically-induced garbage off the control circuit.