The problem with BS1363 and wet areas is the plugs provide very poor hand-to-pin separation and can be a shock risk if handled with wet hands, particularly the rewardable varieties as there are live components very close to the plastic covers and small openings that can easily allow water penetration.

Similar issues apply with all residential plugs/sockets. They're just not suited to that kind of use.

CEEform i.e. IEC/BS/EN 60309 'commando' plugs are the best solution and you should have all of your final circuits protected by a 30mA RCD.