Question

Can UL Listed (Certified) dry type transformers be reversed wired? Does that affect the Listing (Certification)?

Answer

UL Certified (Listed) dry type transformers can only be reverse wired if marked for such use or the installation instructions detail the practice. Dry type power transformers are UL Certified (Listed) under the product category Power and General-Purpose Transformers, Dry Type (XQNX), located on page 567 in the 2014 UL White Book and also in UL’s Online Certifications Directory at www.ul.com/database (enter XQNX at the category code search field).

The Guide Information for XQNX details the required electrical rating markings including the primary voltage and secondary voltage. When reverse-wired, a transformer may experience problems with nuisance tripping of the branch circuit protection due to inrush current. However, users can reverse wire the transformer if it is marked for reverse wiring or the installation instructions provided with the Certified (Listed) transformer indicate that it can be reverse wired per NEC 110.3(B). The Guide Information for XQNX has recently been updated to state: Where the manufacturer permits the transformer be supplied from the marked secondary and loaded from the marked primary, i.e., “reverse-fed” or “bi-directional,” installation instructions shall be provided by the manufacturer detailing how this connection shall be made and specifying any concerns or precautions that should be taken by the installer. The suitability of the installation should be determined by the Authority Having Jurisdiction. The Guide Information for XQNX can be viewed on the UL’s Online Certifications Directory as detailed above.
This is consistent with a new requirement in the 2014 NEC, Section 450.11(B) that states “Source Marking. A transformer shall be permitted to be supplied at the marked secondary voltage, provided that the installation is in accordance with the manufacturer’s instructions.”