You certainly want all of the grounding electrodes bonded together and the water pipe is as good a way as any. Does the pipe run underground between buildings? Connect the second service to the water pipe within 5' of it's entrance to that building. You still need another electrode in both buildings. Water pipes can not be the only electrode.