Reading the ROP to the 1996 where this came from, I say no to both ideas.

Quote
4-112- (230-70(a)): Accept
Note: It was the action of the Technical Correlating Committee
that this Proposal be referred to Code-Making Panels 1, 2, and 10 for
comment.
SUBMIT'rER: Raymond E. Harper, Seattle, WA
RECOMMENDATION: A new paragraph be added to Section 230-
70(a) to read:
Service disconnecting means shall not be installed in the bathrooms.
A bathroom shall be as defined in Section 210-8.
SUBSTANTIATION: Many bathrooms are not readily accessible
when occupied and the door locked. Servicing the unprotected
conductors in such a confined space with the grounded plumbing
fixtures could be hazardous. This is not a proper location for a
service disconnect. This would be in accord with Section 240-24(e).
PANEL ACTION: Accept.
PANEL STATEMENT: The Panel recommends that the Correlating
Committee review this based on the actions of Panel 10 under
Section 240-24(e)


Greg Fretwell