IF the entire sweep is 18" under ground, there is no need to bond that metalic raceway. However, run a metalic riser above grade, and it must be bonded.

This has been the way it is for a longer time than I would care to admit.

BTW, all the MV jobs I have been around are in RGS above ground. 4160, 13.2, etc.




John