I know NEC will allow EMT in concrete with proper corrosion protection, I have always used pvc from day one on the job.
What do you use to install it in the concrete?

I only ask because the SUPER-Foreman on the job I am working at, scoffed at me when I questioned his decision to run emt from parking garage though pan deck up to next level, which they poured the concrete today.

However as I have said before I am in WA state, and we have a state code which supersedes NEC WAC 296-46B-358 which strictly forbids this type of installation not to mention there was no type of corrosion protection talked about in 300.6 just straight EMT(3. I tried to explain that I didn't think this was a good idea...unfortunately as I said he believes he is "Super E"