Looking at this, I don't see how to get around the countertop receptacle requirements.. The backsplash is all lightbox and the cabinets are too high to use plugmold underneath and be considered countertop recepts. I'm guessing they just tied this into existing circuits that were present pre-remodel. Are there ANY places to plug appliances in? I also noticed an island counter which would need an outlet of two..


Was an electrician involved in the hook up of this setup to begin with?

RE: the absence of UL listing.. Would ETL be cheaper and acceptable? (They're the listing on the aftermarket Zinsco, Bulldog, FPE CB's...)

ETL - Intertek

Last edited by Lostazhell; 11/20/12 02:44 AM.