Under 650-7 of the 1999 handbook it reads" Voltage Drop" The voltage at the controller line terminals shall not drop more than 15 percent below normal (controller-rated voltage)under motor starting conditions. The voltage at the motor terminals shall not drop more than 5 percent below the voltage rating of the motor when the motor is operating at 115 percent of the full-load current rating of the motor.


Exception: This limitation shall not apply for emergency run mechanical starting.


There is no "Blue" highlighted wording in the handbook after this section.