Back when all water distribution was metal that was the best grounding electrode. The whole city was tied to the same equipotential grid. Now that everything is plastic that is no longer true so we have the requirement for the supplemental electrode. I would drive a rod and connect it to the panel. If there is any question about the conductivty of the pressure regulator (not all metal body) jumper around it.