I have a 200amp 240v service on a house. 3cc, no need to derate. My breaker have a terminal rating of 75c. Is this a code violation to use 3/0cu thhn


As Bryan (BPHgravity) pointed out, it is Code Compliant on that Residential Feeder to use 2/0 THHN cu for a 200 Amp Circuit.
This is due to the fact that the Feeder will rarely draw anything close to the 200 Amp level, and extremely rare to draw that much of a load for 3 Hours or more.

Even if the example 200 Amp Circuit / Service Feeder was in a Commercial Environment, if there are only 3 CCCs, the Maximum OCPD for the 3/0s may be selected from the 75ยบ column - or Terminated at 200 Amps.

sparkyinak:

Quote

That was a very good write up. Scott


Thanks!!! smile

It has been covered here a few times over the years, so the writing gets easier each time wink

SolarPowered:

*** Per: (if you have questions why 8 CCCs instead of 6, please let me know) ***

Quote

Yes, why? You haven't mentioned that harmonics are an issue, so presumably that's not the reason.


The reason behind this is that most of the time the Common Grounded Conductor will be carrying >= 70% of the highest L-N Load Current value - and more commonly, 100% the highest L-N value.

If the MWBCs are driving Loads which are nearly Pure Resistance, or >.95 PF with very low Harmonic Distortion, then the Common Grounded Conductor will carry a much lower Load Current.
This is not too common - especially in my line of work, so I always consider the Common Grounded Conductor to carry 100% of the highest L-N Load value - when applied to MWBCs (4 Wire Multiwire Branch Circuits).

Of course, any 2 wire L-N Circuit does not have a "Common Neutral", only an Ungrounded Conductor + a Grounded Conductor - so each Conductor is carrying 100% Load Current, and figured as such.

Similar results are encountered with 1 Phase 3 Wire MWBCs from a 3 Phase 4 Wire Wye System.
An L-L-N Circuit is more like a 3 Phase 3 Wire "Open Wye" Circuit - even though it contains a Grounded Conductor from the Star Point of the Secondary Windings.

These MWBCs typically have the higher Load Current value of one given Ungrounded Conductor flowing on the Grounded Conductor.

I can post more information later.

Scott

Last edited by Scott35; 03/16/08 06:53 PM. Reason: inconsistencies