Here are the pics from Ray:

T 1 transformer at Atkinson Rd substation, Titirangi. At the top is the terminal box, the 11 kV cable goes to the back of the TX to the stands LHS, the 33 kV is on the middle near the header tank:

[Linked Image from electricalphotos.com]


Close-up of terminal box and marks from oil vented through gasket:

[Linked Image from electricalphotos.com]


Terminal box open, left hand cable damaged, this being the Blue phase:

[Linked Image from electricalphotos.com]


Terminal box from a different angle:

[Linked Image from electricalphotos.com]


Cable gland removed and cable disconnected from box.
The black pipe was used for bleeding the reservoir.
The red lead was from the 5kV megger:

[Linked Image from electricalphotos.com]


Close-up of damage to the cable:

[Linked Image from electricalphotos.com]


11kV stands, the fault current melted the heatshrink adhesive from the rain-shields on two phases:

[Linked Image from electricalphotos.com]


More to come later......