One question and this is the wrong forum, but I can't say which the right one is.

In my factory, there is a fuse for the earth connection in each building. In each significant one, there is a transformeur 15000V -> 400/230. It uses a system TN-NET and there is an earth fuse outside each building that has a supply like it. So, why is the fuse there, and I wonder what happens if it goes?