As we talked last Saturday NZ / Friday nite USA time I said that I will make a thread re a worked example, so I get my old tech. notes out and have a look and refresh my own memory a bit too. there I don't deal much with PF controls at work.

Example:
A 5 kW motor has a PF of 0.6 with a 240 Volts 50 Hz supply.

Find capacitance required to:
a) increase the PF to unity.
b) increase the PF to 0.9.

Impedance Triangle

......../I
......./.I
....../..I
VA./...I VAr
..../....I
.../.....I
../......I
./.......I
/........I
----------
..Watts..

When the PF is improved, the power of the inductive load remains constant.

PF = true power / apparent power = W / VA.

a) P = 5000 Watts, PF = 0.6, U = 240 Volts.

therefore VA = W / PF = 5000 / 0.6 = 8333.3

and apply pythagoras on the triangle will yield

sq.rt(8333.3²-5000²) = 6666.6 VAr.

to get the PF to unity a capacitance of 6666.6 VAr is required.

VAr = U * Icap. 6666.6 = 240 * Icap. therefore I cap is 27.7 Amps.

Xc = U / I = 240 / 27.7 = 8.64 ohms.
where Xc is reactance of the Capacitor.

C = 1 / (2*pi*f*Xc) = 1 / 2*3.1415*50*8.64 = 368 µF.