PROVIDED that
NONE other than 460V 3ø—3-wire and 1ø—2-wire loads are served, a pair of
properly sized and correctly wired in the right open-delta connection, pair of 1ø units applied similar to that shown on pg 14 of “Three-Phase Ventilated Transformers.” Contact Jefferson Electric
www.jeffersonelectric.com Fuse hiside with dual-element fuses sized per NEC 450-4 and that may adquately protect the secondary and tap conductors also. (If CEC applies, it may apply different rules.)