I get 1.7 amps on the neutral using the calculation I suggested. If your reading 30A with a clamp on meter you ,may have more than that for THD. 60Hz meters are not accurate at frequencies above 60Hz. and Harmonics are multiples of 60.

What are you using to read the neutral current and what is the nature of the load?

Charlie