Folks electure told us it is EMT.

It is not PVC.

It still is a violation.

Quote
The grounding conductor shall be connected as follows:

(1)To the nearest accessible location on the following:

a.The building or structure grounding electrode system as covered in 250.50

b.The grounded interior metal water piping systems, within 1.52 m (5 ft) from its point of entrance to the building, as covered in 250.52

c.The power service accessible means external to the building, as covered in 250.94

d.The metallic power service raceway

e.The service equipment enclosure, or

f.The grounding electrode conductor or the grounding electrode conductor metal enclosures; or

(2)If the building or structure served has no grounding means, as described in 810.21

(F)(1), to any one of the individual electrodes described in 250.52; or

(3)If the building or structure served has no grounding means, as described in 810.21(F)(1) or (F)(2), to an effectively grounded metal structure or to any of the individual electrodes described in 250.52.