German installation again, 30 Year old box with newer additions, 3400W running on this one.

Actually you can close the cover, but as i did after shooting the pic, one of the wires got cut by a terminal of the old porcelain block in the back... BANG.

Violations
- Gn/Ye conductor used as phase (!!!!)
- Red conductor (old GND) used as corresponding wire for a 2-point light switching.
- these #%@€*s built a ground fault, and instead of searching for it, they simply cut the GND wire to get the master GFCI back on. Imagine that!
- fitted 2 cables into one fitting -> lowering the IP class
- Ran into the u-boats from both sides
- violation of my personal point of view: totally bodge. If i had a company and one of my workers did that (the cut gnd thing), i'd kick him out

greetings