a customer called me when the electrician (I use this term cautiously) he hired said they were too busy to get a permit.
pic. #1 they used a 11/4" offset to sleeve into the 2" offset, then used plumbers putty to seal out the weather.
Pic.#2 there is no nipple from the meter to the panel.
Pic#3
our power company requires a 2" rigid conduit when penetrating roofs, and no roof flashing present.
Pic#4 no connectors in panel
Pic#5 the main feeds have no connectors and run in the wall without any conduit.
Pic#6 panel is floating and not secured.
Pic # 7 the final one stranded wire used going up the wall, and a 40 amp breaker with # 12 wire on it for the water heater.
These pictures were taken in a suburb just outside of Dallas. I could not believe the poor and unconcerning workmanship that was done. And there are people living at this home.