More on the subject of temporary wiring by Pierre Belarge

Quote
I knew no one would believe me, so I took the pictures of this installation. Installed by an EC, who actually called for an inspection. The inspector before me almost had a physical fight with the contractor, so he called me. I am known as the "quiet inspector with the sharp pen". The inspection was for a partial rough for a retail store, but I saw a suspect BELL WIRE and asked the contractor what it was for...he shook his shoulders and said "I don't know". Wow he must of thought this was a joke. He was actually stealing power and I guess he knew that he got caught.

The BELL WIRE was spliced (see the small red conductor) into the endline box to the 500 kcmil ahead of the meter or any overcurrent protection. Then the green and white conductors were terminated to the hasp of the endline box for the grounding and neutral connection. It actually worked!!! These pics are not 'touched up', these are actual.

Well the contractor gave me such a hard time (now you know why the other inspector left this to me) that I wrote the violation, walked outside and called the Utility company's Theft of Services Department. They were there faster than you can imagine. His fine and penalty were good enough for him to at least pretend to respect us for the duration of his work on this store.


[Linked Image]


[Linked Image]


[Linked Image]