While troubleshooting an open ground condition on a circuit in my home, I looked in my panel for the first time ... jaw hits floor.

Doorbell transformer inside panel (at bottom)

1 primary lead from x-former wrapped around a wire at breaker, other lead wire-nutted to one of the ground wires sticking out of wire bug

Nothing about this panel very neat or workmanlike

Black friction tape on service neutral

Many grounds too short to reach GND/Neut bar, all wire-bugged to #10 GND of dryer cable

Too much outer jacket insulation on main cable, leads too long

30A DP breaker for hot water tank, using 12-2 w/ GND wire

Panel not clearly or properly labeled

Master bedroom, living room, bathroom, and 1 duplex receptacle in small bedroom all on one circuit (20A) with all 15A receptacles, 15 of them

No separate lighting circuits

White "hot" lead for hot water tank not re-identified

One strand of grounding electrode conductor peeled back and wrapped around other strands (couldn't fit all of them in the hole?)

Front porch light and rest of small bedroom receptacles on same circuit (at opposite ends of house)

Barry P.
Western NY State


[Linked Image]


Joe Tedesco, NEC Consultant