The conduit needs to be effectively bonded to the installed EGC through a bonding bushing because if a fault developed in the raceway, the return path may not have a low enough impedance to assure opening of the OCPD.
Don,
are you wondering if the conduit is effectively bonded at the supply end, and therefore not required to be bonded through a bushing at the switch end?