FPE in Germany pt.2 #220378 12/09/19 02:46 PM
3 Images
Joined: Aug 2008
Posts: 60
A
andey Offline OP
Member
FPE in Germany pt.2

Uploaded for another forum thread
Tools for Electricians:
4 Comments
Re: FPE in Germany pt.2 [Re: andey] #220763 04/29/20 12:22 PM
Joined: Apr 2020
Posts: 9
W
WaterIngress Offline
New Member
Thank you for posting this. Looks like German FPE breaks have a magnetic trip coil not found in the US versions.

Re: FPE in Germany pt.2 [Re: andey] #220770 04/29/20 07:55 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
Can you cite an example of mag trip coil for viewer reference please?

~S~

Re: FPE in Germany pt.2 [Re: andey] #220771 04/29/20 08:18 PM
Joined: Apr 2020
Posts: 9
W
WaterIngress Offline
New Member
Here is an example inside an EU breaker (labelled as a solenoid):

https://www.engineersgarage.com/sit...ageupload/4214/Internal-Parts-of-MCB.jpg


Re: FPE in Germany pt.2 [Re: andey] #220853 06/23/20 07:29 AM
Joined: Aug 2008
Posts: 60
A
andey Offline OP
Member
That is correct, Wateringress. The coil in my photo is on the left side, hidden under the sheet metal fin.

I'm not sure about the whole EU, but all breakers in Germany, since many decades, have these two working mechanisms. The bimetal strip to act time-delayed in overload condition, and the coil for instant trip in short circuit situations. There's different trip curves but the most common curve is "B" where the instant trip will start working at 3 to 5 times the nominal current.
With the most common breaker for regular outlets being B 16 Amp, the fault loop impedance must be low enough to have at very least 80 Amp flow in case of a short, to trigger the instant trip. This is also something the contractor needs to prove by measurement with a special meter.
A common value for the available short circuit current in a regular panel of a German appartment is around 300-2000 Amp. Depending on the distance to the transformer and wiring. So if the wire from the breaker to the outlet is not too long, and terminations are good, you easily make the 80 Amp plus some functional reserve.

Last edited by andey; 06/23/20 07:49 AM.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
NORCAL 3
Popular Topics(Views)
269,982 Are you busy
204,393 Re: Forum
192,611 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3