by tortuga - 03/18/24 08:39 PM
by tortuga - 03/18/24 04:29 PM
Test Post
by sabrown - 03/06/24 05:29 PM
Solar PV Wiring Errors
by renosteinke - 03/02/24 09:12 PM
0 members (), 94 guests, and 11 robots.
Previous Gallery
Next Gallery
#220378 12/09/19 02:46 PM
3 Images
andey Offline OP
FPE in Germany pt.2
Uploaded for another forum thread
4 Comments
Thank you for posting this. Looks like German FPE breaks have a magnetic trip coil not found in the US versions.
Can you cite an example of mag trip coil for viewer reference please?
~S~
Here is an example inside an EU breaker (labelled as a solenoid):
https://www.engineersgarage.com/sit...ageupload/4214/Internal-Parts-of-MCB.jpg
andey Offline OP
That is correct, Wateringress. The coil in my photo is on the left side, hidden under the sheet metal fin.
I'm not sure about the whole EU, but all breakers in Germany, since many decades, have these two working mechanisms. The bimetal strip to act time-delayed in overload condition, and the coil for instant trip in short circuit situations. There's different trip curves but the most common curve is "B" where the instant trip will start working at 3 to 5 times the nominal current.
With the most common breaker for regular outlets being B 16 Amp, the fault loop impedance must be low enough to have at very least 80 Amp flow in case of a short, to trigger the instant trip. This is also something the contractor needs to prove by measurement with a special meter.
A common value for the available short circuit current in a regular panel of a German appartment is around 300-2000 Amp. Depending on the distance to the transformer and wiring. So if the wire from the breaker to the outlet is not too long, and terminations are good, you easily make the 80 Amp plus some functional reserve.