The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 223 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99966 - 09/28/06 12:41 PM Hand book
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Hey I have this fellow electrician. Who claims to have gotten no failures for not using the waterproof bubble very breakable covers. He uses a reference to hand book attended and unattended i`m not sure where he`s coming from but he says no more bubble covers for him. do you guys have a clue where he`s found a loop hole cause I`d like to jump through it also if it flies. Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#99967 - 09/28/06 12:56 PM Re: Hand book
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Either his inspectors are living in the 20th century or he has an old handbook.
Wet location receptacles get a bubble cover here with no real exceptions.
_________________________
Greg Fretwell

Top
#99968 - 09/28/06 12:59 PM Re: Hand book
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Nope new HB 05 but he showed me something about attended and unattended and I think he`s using this reference and has apparently gotten away with it.So I`m looking for it also.

Top
#99969 - 09/28/06 01:10 PM Re: Hand book
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I do not have the 2005 Handbook.

However first and foremost whatever the handbook says is not code and can not be enforced or used as a reason to ignore the 2005 NEC.

In the 2005 NEC you will find 406.8(B)(1) you will find 'bubble covers' are required on every 15 or 20 amp 125 and 250 volt receptacle installed in a wet location.

No Exceptions


Now look at the wording in 406.8(B)(2) it talks about about attended or not attended.

But that section 408.(B)(2) is about 'other receptacles' other being other than 15 or 20 amp 125 and 250 volt receptacles.

So if your installing a 30 amp receptacle in a wet location that will not be used while unattended than you can forget the bubble cover.

15 and 20 amp receptacles still get the bubble.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#99970 - 09/28/06 01:22 PM Re: Hand book
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Iwire what about in HB a and b section on bottom of page 476. Thats the only thing I see that would or could be used.But I see where you are saying other recepticals.I appreciate the feed back. He must have gotten some good donuts that morning

Top
#99971 - 09/28/06 03:21 PM Re: Hand book
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Maybe this guy is installing them in a damp location.

406.8 (A)

Just a thought.