The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
Yesterday at 09:09 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 105 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99819 - 09/18/06 08:15 AM Sub Panel
kyelectric Offline

Registered: 08/30/05
Posts: 64
I was wondering which way is the most common way or best way to feed to a new panel. I am installing a 100 A panel in an detached garage. The feed will come from a 200 A panel in a garage that is close by. There are two ways to do this I believe...First you can run something like USE-2 in a 2-2-2-4 and the 4 can be the grounding conductor for all the circuit grounds as long as the panel does not have the neutrals and grounds bonded. The second way would be to treat it as a new service and run something like 2-2-4 and have the 4 be the grounded conductor and then start a new grounding system there with new ground rods. Which way is best? Thanks.

2014 / 2011 NEC & Related Books and Study Guides
#99820 - 09/18/06 10:06 AM Re: Sub Panel
earlydean Offline

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
The 4-wire connection is the best. A main CB and a grounding electrode system is required in either case. With the three wire connection you have to worry about parallel paths on the grounding electrode system with the grounded conductor. Not a problem with the 4-wire.