#99791 - 09/10/06 08:32 AM Underground pipe - PVC vs Ridgid wrapped
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
I've come across quite a few underground pool pump & light ridgid installations that were correctely wrapped but had rusted out anyway and eventually caused the wires to either short and/or open, and the pool pump quit in residential homes. Usually takes 5 to 10 years.
"I'M SURPRISED THIS IS CODE, I THINK PVC SHOULD BE USED".
No matter how well you wrap it, I think water gets through over time. The soil here in AZ is acidic too.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
2017 / 2014 NEC & Related Books and Study Guides
#99792 - 09/10/06 09:19 AM Re: Underground pipe - PVC vs Ridgid wrapped
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
We have to keep in mind that the NEC is a minimum safety code, not a design manual.

Personally I feel the only use for PVC is underground.

I am not a fan of GRC underground, but I do not feel it should be prohibited.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#99793 - 09/10/06 10:04 AM Re: Underground pipe - PVC vs Ridgid wrapped
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I think it is going to be a local call. In Md I have seen garden variety EMT hold up for a long time underground but like Aldv, here in Florida, even rigid goes pretty fast.
Vote me "plastic" too.
_________________________
Greg Fretwell
Top
#99794 - 09/10/06 10:08 AM Re: Underground pipe - PVC vs Ridgid wrapped
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
gfretwell, I agree..
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#99795 - 09/10/06 11:48 AM Re: Underground pipe - PVC vs Ridgid wrapped
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
Concrete encased pvc buried pipe gets my votiest vote of all.
Top
#99796 - 09/10/06 06:05 PM Re: Underground pipe - PVC vs Ridgid wrapped
Fred Offline
Member
Registered: 04/30/01
Posts: 449
Loc: Straughn, IN 47387
I prefer PVC for underground work. We just installed 500' of 4" sched 80 in 3 parallel runs Friday. They ran from the padmount transformer to the future mechanical room location for a church addition. We put them 66" below the pad and bedded them in 24" of coarse sand before backfilling. Nobody should come near these pipes, but if they do they are going to see sand before they hit PVC, I hope. The same excavator is doing all of the digging on this job. My conduits under the slab will be done the same way only they will be 48" below the slab. Well below the plumber's drains.
Top
#99797 - 09/11/06 07:47 AM Re: Underground pipe - PVC vs Ridgid wrapped
Zapped Offline
Member
Registered: 10/01/02
Posts: 482
Loc: Huntington Beach, CA, USA
Out here in Orange County, CA, I try to use nothing but PVC underground. Not only is the soil super acidic (especially near the ocean), but alot of the irrigation systems are run with reclaimed water - metal of any kind doesn't stand a chance. I've even run across rubberized-rigid that corroded right inside the rubber from a leak at one of the joints, and just disolved into oblivion.

Concrete-encased PVC is nice, as it's basically just a plastic-lined concrete conduit. I've seen this in the snack bars that are actuall ON the beach. Works great until a plumber comes along with a concrete saw... Gotta love plumbers, they keep my bills paid =)
Top
#99798 - 09/11/06 05:53 PM Re: Underground pipe - PVC vs Ridgid wrapped
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Zapped, You're from HB!

GRC, IMC, or EMT aren't even permitted to be installed outdoors abovegroundin your town unless they are painted with a marine grade paint (that's about $65 a gallon).
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals