#99777 - 09/06/06 04:19 PM Spa and Hot Tub Disconnect
Tiger Offline
Member
Registered: 05/04/05
Posts: 706
Loc: Crystal Lake, IL USA
Is there a requirement that a spa or hot tub disconnect be over 5' from the spa? The conditions are as follows:

Single-family dwelling
Outdoor location

Article 680.12 only mentions "accessible and within sight", however Exhibit 680.2 mentions "at least 5 ft. from the pool".

Dave
Top
2017 / 2014 NEC & Related Books and Study Guides
#99778 - 09/06/06 05:13 PM Re: Spa and Hot Tub Disconnect
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
680.22 says all switching devices will be 5' or greater from the water.
There is still some debate about a disconnect under the covers of the spa.
_________________________
Greg Fretwell
Top
#99779 - 09/06/06 05:53 PM Re: Spa and Hot Tub Disconnect
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
I have wondered why you can install a light switch as close as you want to a hydromassage tub, but not for an indoor spa?
Top
#99780 - 09/06/06 09:04 PM Re: Spa and Hot Tub Disconnect
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I got spanked here a while ago for confusing the hydromassage tub rules and the spa rules. They are basically just a bathtub.
_________________________
Greg Fretwell
Top
#99781 - 09/09/06 06:06 PM Re: Spa and Hot Tub Disconnect
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
I believe the 5' rule is so Joe Homeowner doesn't mess with the disconnect while he or she is actually in the spa. I know common sense tells us that water and electricity DO NOT MIX but some homeowners are no-so-bright when it comes to electrical issues.
Top
#99782 - 09/26/06 01:04 PM Re: Spa and Hot Tub Disconnect
Tripp Offline
Member
Registered: 09/20/05
Posts: 99
The article cited by gfretwell (680.22 (C)) actually pertains to "II. Permanently Installed Pools", which is a section separate from "IV. Spas and Hot Tubs." The closest the NEC comes to stating a required distance for the disconnect, aside from the "readily accessible and within sight" requirement in 680.12, is the 5' required for an "Emergency Switch" in 680.41; but this "emergency switch" is not the same as the "maintenance disconnect," AND the article concludes with the statement that "This requiremnet shall NOT apply to single-family dwellings."

So to summarize, all we get from the NEC, regarding home hot tubs, is "readily accessible and within sight." For more specifics you need to talk to your AHJ.
Top
#99783 - 09/26/06 01:48 PM Re: Spa and Hot Tub Disconnect
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Tripp- The text at 680.12 is for a Maintenance Disconnect Switch not the "Emergency Switch" and applies to all equipment in 680 unless altered by some other section in 680.

The rules in 680.20(C) apply to Spas installed outside. See 680.42. gfretwell is correct.
_________________________
George Little
Top
#99784 - 09/26/06 04:24 PM Re: Spa and Hot Tub Disconnect
Tripp Offline
Member
Registered: 09/20/05
Posts: 99
George: I stand humbly corrected. I am embarrassed to realize (and in public!) that i have never noticed that 680.42 references Parts I AND II. I've always just noticed the article above (680.41) that references Parts I and IV and called it good.

So putting my humiliation aside, let me ask you this: are you saying that "Switching Devices" (per 680.22 (C)) includes Maintenance Disconnects? If so, why don't they just spell it out like they do in the General section 680.12 Maintenance Disconnects?

Thanks for being gentle.
Top
#99785 - 09/26/06 04:26 PM Re: Spa and Hot Tub Disconnect
Tripp Offline
Member
Registered: 09/20/05
Posts: 99
And apologies to gfretwell.
Top
#99786 - 09/26/06 06:34 PM Re: Spa and Hot Tub Disconnect
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
No problem at all. I screw up things here too. That is why it is good to be with friends. Greg
_________________________
Greg Fretwell
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 121 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals