The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 245 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99771 - 09/04/06 08:32 PM Does 352.12 trump 314.23(E)&(F)?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
314.23(E)&(F) says you can support enclosures from raceways and 352.12(B) referencing 352.10(H) says you can't support anything but conduit bodies from RNC. Can you support a swimming pool wet niche "J" box from RNC? How about a transformer?

I know we routinely OK the J box. Is it really a violation?
_________________________
Greg Fretwell

Top
2014 / 2011 NEC & Related Books and Study Guides
#99772 - 09/05/06 03:58 AM Re: Does 352.12 trump 314.23(E)&(F)?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The specific rules always "trump" the general rules.
Don

[This message has been edited by resqcapt19 (edited 09-05-2006).]
_________________________
Don(resqcapt19)

Top
#99773 - 09/05/06 09:06 AM Re: Does 352.12 trump 314.23(E)&(F)?
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
No, you cannot support neither a deck box or a transformer with PVC conduit. 90.3 tells us that information in Chapters 1-4 apply generally, and Chapters 5-7 supplement or modify the general rules.
314.23(E)&(F) tells us we can support a splicing device with RMC or IMC conduit (the only 2 wiring methods that can be threaded wrenchtight).
352.10(H) allows conduit bodies containing splicing devices (wire-nuts).
Both transformers and deck boxes need to be listed (680.24) Nowhere in 680.24 does it allow the PVC conduit to support the deck box or transformer.

It really is a violation!


[This message has been edited by earlydean (edited 09-05-2006).]
_________________________
Earl

Top
#99774 - 09/05/06 11:37 AM Re: Does 352.12 trump 314.23(E)&(F)?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The PVC J boxes really do not have a place to provide additional support.
Usually they do just get stuck up on the stubs that come out of the ground. If the pool is built on a stem wall and the equipment is on the ground these can be on some pretty tall pipes. I have never liked it but it is SOP. The other day I had a fellow IAEI inspector say the same rule would allow a transformer if it was made of a suitable material with threaded hubs. I drew the line there. I see you agree with my original contention, that the J boxes were also illegal, although I don't know how else you would do it.
Mine are really supported by the RNC but I have a clamp within an inch of the J box and they are against the wall.
_________________________
Greg Fretwell

Top
#99775 - 09/05/06 12:39 PM Re: Does 352.12 trump 314.23(E)&(F)?
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
There's some Listed equipment out there made by I think a company called "Thermcraft" and sold through T & B. The deck boxes are supported by an optional solid post or an optional bracket suport. They also are Listed for multiple lights with terminations for more than one fixture. I saw them when I was at the Jubilee in FL. Greg you might remember the booth where the guy was pushing their products.
Found a site that I was talking about: http://www.californiapoolsupply.net/Ther..._p/jbp57510.htm

[This message has been edited by George Little (edited 09-05-2006).]
_________________________
George Little

Top
#99776 - 09/05/06 07:54 PM Re: Does 352.12 trump 314.23(E)&(F)?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Interesting George. The Thermocraft is the box we see but I never see the support hardware. Usually it is just a 1x3 PT scrap they find in the dumpster from the window framers and strapped to the raceways.

(Yeah I suppose they might bring a 1x3 but I doubt it)