The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
Today at 01:42 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (Webmaster, LongRunner), 227 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99768 - 09/04/06 08:10 PM What is 225.38(C) trying to say
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Why should you need to disconnect the grounded conductor?
_________________________
Greg Fretwell

Top
2014 / 2011 NEC & Related Books and Study Guides
#99769 - 09/05/06 02:12 AM Re: What is 225.38(C) trying to say
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
You might want to pull it for testing purposes.

If you are looking for illegal ground to neutral connections lifting the neutral would be step one along with the MBJ.

That said I don't understand what it really accomplishes, I have never seen any one in the field talk about it. It seems more of a construction specification of service rated equipment. 225.36

Now when we use the exception to 225.36 do we need to use two pole snap switches so we can break both grounded and ungrounded conductors simultaneously?

FWIW 225.38(C) mirrors 230.75
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#99770 - 09/05/06 04:22 AM Re: What is 225.38(C) trying to say
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
We've got a couple of jurisdictions here in SoCA that have you perform a "neutral to ground" continuity test (with the link removed) at final inspection.
This way they can verify that there are no grounding connections on the neutral anyplace but where they belong....At the service.
Resi services are done with the individual neuts disconnected from the neutral bar.

A good idea, IMO