A group of say 9 apartment buildings (6-12 separate entrance apartments). I need a small house feeder/panelboard to each building for outside lights and other minor house loads.
Each building will have the 6-12 meters for the tenants.
Can we install one house service meter on one of the buildings and run feeders to the other buildings for the house load?
The buildings are all owned and maintained by one owner.
Top
2017 / 2014 NEC & Related Books and Study Guides
#99745 - 09/03/06 06:06 AM Re: One house service for multiple apartment bldgs
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Look at 225.30 and talk to the AHJ and possibly you will have a solution.
_________________________
George Little
Top
#99746 - 09/03/06 11:27 AM Re: One house service for multiple apartment bldgs
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Florida IAEI guys had a similar discussion and ended up with the opinion that convenience was not a good enough reason to allow multiple feeders into a building.
They wanted separate meters on a single service in each building.
_________________________
Greg Fretwell
Top
#99747 - 09/03/06 05:42 PM Re: One house service for multiple apartment bldgs
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
I thought it was pretty well covered in the NEC but reading it again, I am getting a bad feeling about it. I will call an inspector ASAP.
Each separate building would have one service (230.2) plus a feeder (225.30).
Top
#99748 - 09/04/06 04:16 AM Re: One house service for multiple apartment bldgs
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
IMO The inspector might allow it per 225.30(D) I would certainly talk to them about it beforehand.

If you are allowed to do this you will be required by 225.31 to install a disconnecting means, that disconnecting means would have to be service rated per 225.36.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#99749 - 09/04/06 06:55 PM Re: One house service for multiple apartment bldgs
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Bob- (iWire) That's what I was thinking. In the interest of safety and not creating a monster of an expense I could see a contractor using 225.30(D) and applying some good signage and I would pass it if it were in my jurisdiction. Of course he would need to use the rules you mentioned in 225.31 also.
_________________________
George Little
Top
#99750 - 09/16/06 02:18 PM Re: One house service for multiple apartment bldgs
tdhorne Offline
Member
Registered: 03/22/01
Posts: 345
Loc: Maryland, USA
If you have any form of emergency supply for the house panel feeder then there will be no question as to the legality of using a feeeder instead of a service. You could pay for the cost of a small generator by just the savings on the multiple meter fees.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 30 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals