The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99744 - 09/03/06 05:18 AM One house service for multiple apartment bldgs
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
A group of say 9 apartment buildings (6-12 separate entrance apartments). I need a small house feeder/panelboard to each building for outside lights and other minor house loads.
Each building will have the 6-12 meters for the tenants.
Can we install one house service meter on one of the buildings and run feeders to the other buildings for the house load?
The buildings are all owned and maintained by one owner.

Top
2014 / 2011 NEC & Related Books and Study Guides
#99745 - 09/03/06 06:06 AM Re: One house service for multiple apartment bldgs
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Look at 225.30 and talk to the AHJ and possibly you will have a solution.
_________________________
George Little

Top
#99746 - 09/03/06 11:27 AM Re: One house service for multiple apartment bldgs
gfretwell Online   content

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Florida IAEI guys had a similar discussion and ended up with the opinion that convenience was not a good enough reason to allow multiple feeders into a building.
They wanted separate meters on a single service in each building.
_________________________
Greg Fretwell

Top
#99747 - 09/03/06 05:42 PM Re: One house service for multiple apartment bldgs
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
I thought it was pretty well covered in the NEC but reading it again, I am getting a bad feeling about it. I will call an inspector ASAP.
Each separate building would have one service (230.2) plus a feeder (225.30).

Top
#99748 - 09/04/06 04:16 AM Re: One house service for multiple apartment bldgs
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
IMO The inspector might allow it per 225.30(D) I would certainly talk to them about it beforehand.

If you are allowed to do this you will be required by 225.31 to install a disconnecting means, that disconnecting means would have to be service rated per 225.36.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#99749 - 09/04/06 06:55 PM Re: One house service for multiple apartment bldgs
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Bob- (iWire) That's what I was thinking. In the interest of safety and not creating a monster of an expense I could see a contractor using 225.30(D) and applying some good signage and I would pass it if it were in my jurisdiction. Of course he would need to use the rules you mentioned in 225.31 also.
_________________________
George Little

Top
#99750 - 09/16/06 02:18 PM Re: One house service for multiple apartment bldgs
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
If you have any form of emergency supply for the house panel feeder then there will be no question as to the legality of using a feeeder instead of a service. You could pay for the cost of a small generator by just the savings on the multiple meter fees.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison