#99703 - 08/30/06 10:02 PM disconnecting means for Shore receptacles for ships
ih17dka8 Offline
Junior Member
Registered: 01/16/06
Posts: 8
Loc: Seoul, South Korea
Could push button connected to shunt trip coils be the disconnecting means for shore receptacles per NEC 555.17(B)? That's kind of remote contact to trip the circuit breaker for shore receptacles(500A).

------------------------------------------
NEC 555.17(B)Location. The disconnecting means shall be readily accessible, located not more than 762 mm (30 in.) from the receptacle it controls...
Top
2017 / 2014 NEC & Related Books and Study Guides
#99704 - 08/31/06 09:11 AM Re: disconnecting means for Shore receptacles for ships
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I believe the intent is that the user will be able to connect the shore tie cable without power being applied and then turn it on. How would you turn the shunt trip breaker back on ?
_________________________
Greg Fretwell
Top
#99705 - 08/31/06 10:36 AM Re: disconnecting means for Shore receptacles for ships
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I just went to several sources for the recomended procedures for checking shore ties and they all concur that you must turn off the power at the shore post and the breakers in the boat before you plug in the cable. Then you turn on the shore power, verify the polarity indicators in the boat read OK then turn on the boat breakers.
You could not use a shunt trip for the post and follow this procedure without taking a long walk to a location you may not be aware of. That would encourage people to handle a hot cable in a wet environment. Bad idea.
_________________________
Greg Fretwell
Top
#99706 - 09/02/06 01:05 PM Re: disconnecting means for Shore receptacles for ships
mhulbert Offline
Member
Registered: 10/19/04
Posts: 132
Loc: Anaheim, CA USA
What about a motor operated breaker with a remote open/close selctor switch, and indicator lights and/or meters to verify zero volts? What type of connectors are you using at 500A? Cam Lock?

Motor operated is expensive, but it might be cheaper than an extra 600A disconnect.
Top
#99707 - 09/03/06 11:21 AM Re: disconnecting means for Shore receptacles for ships
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I agree that would meet the intent of the code.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ghost307), 67 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals