The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by Texas_Ranger
24 minutes 10 seconds ago
100% breakers?
by Texas_Ranger
28 minutes 26 seconds ago
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 10
Trumpy 8
Who's Online
2 registered (LongRunner, Texas_Ranger), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99694 - 08/30/06 05:56 AM Non-Fusible Service Disconnects
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
Please give an example of where a non-fusible service disconnect can be used.

Thank you

[This message has been edited by Frank Cinker (edited 08-30-2006).]

Top
2014 / 2011 NEC & Related Books and Study Guides
#99695 - 08/30/06 10:27 AM Re: Non-Fusible Service Disconnects
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Frank,
The only way you can do that is if you put the OCPD immediately adjacent thereto. 230.91
Don
_________________________
Don(resqcapt19)

Top
#99696 - 08/30/06 01:58 PM Re: Non-Fusible Service Disconnects
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
As a "utility company" disconnect ahead of a meter socket it must be rated for service duty. They do not have OCP and are not the "service disconnect".
They are frequently used where a standard pull out meter socket is used for 480 V 3 phase, corner grounded, 200 amp or less on sewer lift stations. After the meter is the "service disconnect".
Bonding and grounding confusion with this kind of installation is extensive.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.

Top