The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 221 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#99671 - 08/29/06 04:25 AM feeder protection
carranoelectric Offline
Junior Member

Registered: 08/28/06
Posts: 4
Loc: stratford ct
Is the secondary feeder from a 75 kva xfrm protected from the primary breaker? I have a 100 amp 480 v breaker on the primary with a 200 amp 208 v secodary to a panel. Do I need a 200 amp main or can I use main lug and have the 100 amp breaker protect the 200 amp feeder?

Top
2014 / 2011 NEC & Related Books and Study Guides
#99672 - 08/29/06 05:16 AM Re: feeder protection
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
Proably not, and in this case I believe "NO" The OCPD installed per 450.3B protects the transformer proper, The secondary conductors are Tap conductors and must be protected in accordance with 240.21 (C)

Charlie

Top
#99673 - 08/29/06 05:18 AM Re: feeder protection
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
If this is a lighting and appliance BC panel board you must have not more than two mains, no MLO,

Charlie

Top
#99674 - 08/29/06 12:49 PM Re: feeder protection
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
The truth of the matter is if it's a single voltage secondary and a 3 phase Delta you can protect the secondary conductors with overcurrent protection on the primary. You could even use a MLO panel. Chances are tho, you have a secondary that would be more than one voltage and you need to protect the secondary conductors at their ampacity. You will be using the transformer tap rules in Article 240 for protecting these conductors. As for protecting the secondary of the transformer, you can protect it via the overcurrent protection on the primary sized @ 125% or limit the load on the secondary to the ampacity of the secondary with no more than 6 taps to overcurrent protection that does not exceed the ampacity of the secondary of the transformer.
_________________________
George Little

Top
#99675 - 08/29/06 01:24 PM Re: feeder protection
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
By "single voltage delta" I guess you mean corner ground
_________________________
Greg Fretwell

Top
#99676 - 08/29/06 04:10 PM Re: feeder protection
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
Greorge
I'm not sure that you can go MLO if the panel qualifies as a lighting and appliance BC panel board .

Charlie

Top
#99677 - 08/29/06 04:49 PM Re: feeder protection
Dave T Offline
Member

Registered: 01/22/05
Posts: 157
Loc: Waukesha, WI, USA
It is if my opinion that there is a lot of info missing such as if it's a 1ph 480-208v transformer with a 2w secondary(probably not though), a 480v 3ph delta-208vdelta (probably not either, but a educated "guess" would assume that it is a common 74kva 480v-208y/120 with a 3ph4w secondary which means that it would have both pri. and sec. OCPDs.
As a former application engineer to provide an answer based upon incomplete information as illustrated with this question is not wise.

Top
#99678 - 08/30/06 04:21 AM Re: feeder protection
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Charlie,
 Quote:
I'm not sure that you can go MLO if the panel qualifies as a lighting and appliance BC panel board.

If you are working on one of those somewhat rare cases where the transformer primay OCPD is permitted to protect the secondary conductors, then you would have overcurren protection on the line side of the lighting and appliance branch cicuit panel board as required by 408.36(A).
Don
_________________________
Don(resqcapt19)

Top
#99679 - 08/30/06 02:34 PM Re: feeder protection
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
Don I believe you are refering to 240.21(C) (5)???

I haven't given that application much thought but it is interesting


Charlie

Top
#99680 - 08/30/06 03:26 PM Re: feeder protection
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
carranoelectric,

I made a reply to this question at the Electrical Theory and Applications section.

The thread may be accessed using the following link:

Feeder Protection

or the "boring old, long version":
http://electrical-contractor.net/ubb/Forum7/HTML/000526.html

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top