#99671 - 08/29/06 04:25 AM feeder protection
carranoelectric Offline
Junior Member
Registered: 08/28/06
Posts: 4
Loc: stratford ct
Is the secondary feeder from a 75 kva xfrm protected from the primary breaker? I have a 100 amp 480 v breaker on the primary with a 200 amp 208 v secodary to a panel. Do I need a 200 amp main or can I use main lug and have the 100 amp breaker protect the 200 amp feeder?
Top
2017 / 2014 NEC & Related Books and Study Guides
#99672 - 08/29/06 05:16 AM Re: feeder protection
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
Proably not, and in this case I believe "NO" The OCPD installed per 450.3B protects the transformer proper, The secondary conductors are Tap conductors and must be protected in accordance with 240.21 (C)

Charlie
Top
#99673 - 08/29/06 05:18 AM Re: feeder protection
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
If this is a lighting and appliance BC panel board you must have not more than two mains, no MLO,

Charlie
Top
#99674 - 08/29/06 12:49 PM Re: feeder protection
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
The truth of the matter is if it's a single voltage secondary and a 3 phase Delta you can protect the secondary conductors with overcurrent protection on the primary. You could even use a MLO panel. Chances are tho, you have a secondary that would be more than one voltage and you need to protect the secondary conductors at their ampacity. You will be using the transformer tap rules in Article 240 for protecting these conductors. As for protecting the secondary of the transformer, you can protect it via the overcurrent protection on the primary sized @ 125% or limit the load on the secondary to the ampacity of the secondary with no more than 6 taps to overcurrent protection that does not exceed the ampacity of the secondary of the transformer.
_________________________
George Little
Top
#99675 - 08/29/06 01:24 PM Re: feeder protection
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
By "single voltage delta" I guess you mean corner ground
_________________________
Greg Fretwell
Top
#99676 - 08/29/06 04:10 PM Re: feeder protection
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
Greorge
I'm not sure that you can go MLO if the panel qualifies as a lighting and appliance BC panel board .

Charlie
Top
#99677 - 08/29/06 04:49 PM Re: feeder protection
Dave T Offline
Member
Registered: 01/22/05
Posts: 155
Loc: Waukesha, WI, USA
It is if my opinion that there is a lot of info missing such as if it's a 1ph 480-208v transformer with a 2w secondary(probably not though), a 480v 3ph delta-208vdelta (probably not either, but a educated "guess" would assume that it is a common 74kva 480v-208y/120 with a 3ph4w secondary which means that it would have both pri. and sec. OCPDs.
As a former application engineer to provide an answer based upon incomplete information as illustrated with this question is not wise.
Top
#99678 - 08/30/06 04:21 AM Re: feeder protection
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Charlie,
Quote:
I'm not sure that you can go MLO if the panel qualifies as a lighting and appliance BC panel board.

If you are working on one of those somewhat rare cases where the transformer primay OCPD is permitted to protect the secondary conductors, then you would have overcurren protection on the line side of the lighting and appliance branch cicuit panel board as required by 408.36(A).
Don
_________________________
Don(resqcapt19)
Top
#99679 - 08/30/06 02:34 PM Re: feeder protection
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
Don I believe you are refering to 240.21(C) (5)???

I haven't given that application much thought but it is interesting


Charlie
Top
#99680 - 08/30/06 03:26 PM Re: feeder protection
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
carranoelectric,

I made a reply to this question at the Electrical Theory and Applications section.

The thread may be accessed using the following link:

Feeder Protection

or the "boring old, long version":
http://electrical-contractor.net/ubb/Forum7/HTML/000526.html

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 63 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals