The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Ruben Rocha
Today at 07:36 PM
ESA Arc flash course
by frank
Today at 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 27
HotLine1 21
Ruben Rocha 16
Trumpy 12
ghost307 12
Who's Online
2 registered (Webmaster, sparkyinak), 0 Guests and 223 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99667 - 08/25/06 05:21 PM Slaughter House/Meant packing Plant
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Any reason a Slaughter House/ Meat packing plant can't be wired all in P.V.C. ?? (For washdown purposes mainly.

Top
2017 / 2014 NEC & Related Books and Study Guides
#99668 - 08/26/06 08:16 AM Re: Slaughter House/Meant packing Plant
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
No reason at all, according to the NEC. Actually, this is a very wet, corrosive place, and PVC might be a good idea.

That said... make sure the USDA inspector agrees!

Top
#99669 - 08/26/06 01:12 PM Re: Slaughter House/Meant packing Plant
livetoride Offline
Member

Registered: 01/11/05
Posts: 109
Loc: san diego ca usa
The meat packing places I have done PVC is required. You also have to use clamps that hold the conduit off the wall. I use 2 hole PVC straps that suround the pipe, they hold the conduit 1/8" off the wall so the pipe does not trap crud aganst the wall. Rod http://www.plumbingsupply.com/pipeclamps.html edit to add link

[This message has been edited by livetoride (edited 08-26-2006).]

Top
#99670 - 08/27/06 06:55 PM Re: Slaughter House/Meant packing Plant
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Quote:
they hold the conduit 1/8" off the wall


Keep in mind that you need a 1/4" space behind the conduit unless it's nonmetallic conduit mounted to concrete, masonry, tile, or a similar surface.

See 300.6(D)

Top