The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (gfretwell), 313 Guests and 3 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99667 - 08/25/06 05:21 PM Slaughter House/Meant packing Plant
Yoopersup Offline

Registered: 03/04/03
Posts: 826
Loc: Michigan
Any reason a Slaughter House/ Meat packing plant can't be wired all in P.V.C. ?? (For washdown purposes mainly.

2014 / 2011 NEC & Related Books and Study Guides
#99668 - 08/26/06 08:16 AM Re: Slaughter House/Meant packing Plant
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
No reason at all, according to the NEC. Actually, this is a very wet, corrosive place, and PVC might be a good idea.

That said... make sure the USDA inspector agrees!

#99669 - 08/26/06 01:12 PM Re: Slaughter House/Meant packing Plant
livetoride Offline

Registered: 01/11/05
Posts: 109
Loc: san diego ca usa
The meat packing places I have done PVC is required. You also have to use clamps that hold the conduit off the wall. I use 2 hole PVC straps that suround the pipe, they hold the conduit 1/8" off the wall so the pipe does not trap crud aganst the wall. Rod edit to add link

[This message has been edited by livetoride (edited 08-26-2006).]

#99670 - 08/27/06 06:55 PM Re: Slaughter House/Meant packing Plant
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
they hold the conduit 1/8" off the wall

Keep in mind that you need a 1/4" space behind the conduit unless it's nonmetallic conduit mounted to concrete, masonry, tile, or a similar surface.

See 300.6(D)