#99636 - 08/22/06 11:47 AM Classroom confusion  
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
This is the situation.
Portable classroom composed of two halves, (think of a double wide mobile home) each with a 100 amp main breaker panel that controls the circuits in that half of the building.
The electrician brings TWO 100 amp feeders out to the panels. Each originates in the same service panel with a 2pole 100 breaker.
Based on 225.30 (formerly 225.8 & 9[1996] and 230.84[1990]) only ONE feeder or branch circuit, with exceptions for firepumps etc.
To comply with the Code should the electrician (1) use a 200 amp breaker listed for two conductors per pole (2) handle tie the two 100 amp breakers, (3) either or (4)something else ?
Note the panels inside are ten feet apart.
We build them around here and use them but, I'm just not sure. [Linked Image]
Alan--


Alan--
If it was easy, anyone could do it.

2017 / 2014 NEC & Related Books and Study Guides

#99637 - 08/22/06 12:56 PM Re: Classroom confusion  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
I would supply a small 150-200 amp main breaker panel mounted on the outside of the classroom, then feed each panel with a 100 amp feeder. Maybe even supply a branch circuit for outside lighting.

It may be, that when the calculations are done for the combined load of both halves, that a 100 amp feeder would suffice. If so, then you could feed the closer panel, and subfeed the other from the first.


Earl

#99638 - 08/22/06 03:44 PM Re: Classroom confusion  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I'm thinking a single 200 amp feeder run to a 200 amp disconnect mounted inside or outside the structure. If you feel that the two inside panels are "grouped" as required by 225.34(A), then the feeder can be run to the structure and then tapped at that point.


Few things are harder to put up with than the annoyance of a good example.

#99639 - 08/24/06 02:09 PM Re: Classroom confusion  
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
Problem solved [Linked Image]
One disconnect, (service or not) rated 200 amps (225.30 & 34) with one feeder to each double classroom.
At the classrooms a W.P. junction box with two 100 amp taps (per 240.21 tap rule) to the panels.
Done & Done.
Alan--


Alan--
If it was easy, anyone could do it.

#99640 - 08/24/06 03:13 PM Re: Classroom confusion  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
And don't forget to install a couple of ground rods.


Earl


Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,428
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7663 MB (Peak: 0.9020 MB) Zlib enabled. Server Time: 2017-03-27 08:30:24 UTC