#99615 - 08/18/06 11:41 AM 517.13 Grounding of Receptacles in Patient Care Areas
Takideezy Offline
Junior Member
Registered: 08/03/06
Posts: 9
Loc: Williamsport,PA,USA
I am working on an Audiologist office, this is new construction. i believe that the patient examination area requires branch circuits to be wired per 517.13. Based on the installation requirements I plan to use Type AC cable that contains an insulated equipment grounding (bonding) conductor, marked as HFC- Health Care Facility Cable.

I'm stuck on the bonding requirements at the panel and the boxes where "hospital grade" receptacles will be installed on branch circuits. Is there a specific requirement for bonding to insure the redundant ground path is maintained? Are there specific cable clamps/connectors to be used with this cable?

Thanks for the help. Mike
Top
2017 / 2014 NEC & Related Books and Study Guides
#99616 - 08/18/06 12:18 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas
raider1 Offline
Member
Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
Quote:
Is there a specific requirement for bonding to insure the redundant ground path is maintained? Are there specific cable clamps/connectors to be used with this cable?


You must follow the manufactures listing requirments for termination of the cable. With that said most of the time you don't have to do anything with the bond wire but to cut it off or wrap it back over the cable sheath.

As for special connectors, all you need are connectors that are listed for use with AC cable.

Chris
Top
#99617 - 08/18/06 12:58 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Along with Chris's post, the insulated EGC is the only conductor that will attach to the box and the device, the same as any installation.

Are the HG devices being used for an engineers specification? If these rooms are just exam rooms they will not need HG devices as far as the NEC or NFPA 99 is concerned.

Roger
Top
#99618 - 08/18/06 01:45 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas
Takideezy Offline
Junior Member
Registered: 08/03/06
Posts: 9
Loc: Williamsport,PA,USA
It was my assumption that HG devices were required. However after re-reading 517.13B all it requires is that the grounding conductor be insulated and copper. I was likely also influenced by 517.16. Thanks Roger for the clarification. Anything else I'm missing?

Mike
Top
#99619 - 08/18/06 05:53 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Mike, I can't think of anything else at the moment.

BTW, welcome to the forum.

Roger
Top
#99620 - 08/18/06 06:52 PM Re: 517.13 Grounding of Receptacles in Patient Care Areas
Takideezy Offline
Junior Member
Registered: 08/03/06
Posts: 9
Loc: Williamsport,PA,USA
Thanks Roger - It's a great forum. I have been lurking for a while. Mike
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals