The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 170 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 4 1 2 3 4 >
Topic Options
Rate This Topic
#99579 - 08/17/06 07:01 PM multiwire circuits and tied breakers
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
My registeration expired or i could not use my existing ID and/or password so i had to register again.

My ispection was failed because the inspector said all multiwire branch circuit that share a neutral must be on a tied breaker.

In my situation i had two single breakers on two different busbars feeding two receptacles for garebage disposer and the washing machine.

My understanding is whenever there is a peotential difference between the ungrounded conductors on one device then the breaker has to be tied.

Is he correct in his statement?

Thanks
Edward
_________________________
Be kind to your neighbor, he knows where you live


Top
2014 / 2011 NEC & Related Books and Study Guides
#99580 - 08/17/06 07:11 PM Re: multiwire circuits and tied breakers
macmikeman Offline
Member

Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
In my opinion he is incorrect. As long as the two breakers are on opposing poles of the panel buss there is no code violation until they are feeding a single yolk. If they are not feeding a single yolk device than they can be 1,3,5,7,9, etc spaces apart, but I would have them right next to each other.

Top
#99581 - 08/17/06 08:19 PM Re: multiwire circuits and tied breakers
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Remember also that, when NOT using handle-tied breakers, that every neutral connection cannot depend on the receptacle screws, but must be joined, and terminals pigtailed.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#99582 - 08/17/06 09:22 PM Re: multiwire circuits and tied breakers
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Larry, I ALWAYS- ALWAYS make pigtails.

If you think the inspector is right or has an argument please give me a code reference i can not find any NEC reference that supports his statement.

Thanks
Edward
_________________________
Be kind to your neighbor, he knows where you live


Top
#99583 - 08/17/06 09:42 PM Re: multiwire circuits and tied breakers
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Edward

Did you mean disposal and dishwasher ? Are you feeding a single split wired duplex receptacle with this circuit? If you are feeding a split wired duplex with this circuit you need a handle tie or a 2 pole breaker. As long as both of these circuits do not connect to a single device (yoke) you don’t need a handle tie or 2 pole breaker.

What city is this in?

Curt
_________________________
Curt Swartz

Top
#99584 - 08/17/06 10:53 PM Re: multiwire circuits and tied breakers
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Curt,

It is San Jose.

I always use two separate receptacles.
The inspector said everytime you have multiwire branch circuits and share a neutral, you must use tied breakers.

???????

Thankx
edward
_________________________
Be kind to your neighbor, he knows where you live


Top
#99585 - 08/17/06 11:01 PM Re: multiwire circuits and tied breakers
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
I'm sure this was a combo inspector. Call the city and ask to speak with the electrical supevisor for the area your project is in. Don't change the breaker just to make him happy.

Curt
_________________________
Curt Swartz

Top
#99586 - 08/18/06 10:36 AM Re: multiwire circuits and tied breakers
trobb Offline
Member

Registered: 06/08/06
Posts: 111
Loc: Iowa City, IA
The flat I just moved out of had this configuration- common duplex receptacle feeding a dishwasher and a disposal, two circuits, handle tied. For me, it makes sense because this way you won't run into a half-dead box assuming it's fully dead.

Top
#99587 - 08/18/06 02:38 PM Re: multiwire circuits and tied breakers
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
Remember also that, when NOT using handle-tied breakers, that every neutral connection cannot depend on the receptacle screws, but must be joined, and terminals pigtailed.


This applies handle ties or not.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#99588 - 08/18/06 03:23 PM Re: multiwire circuits and tied breakers
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Right you are!

300.13 Mechanical and Electrical Continuity — Conductors.

(B) Device Removal. In multiwire branch circuits, the continuity of a grounded conductor shall not depend on device connections such as lampholders, receptacles, and so forth, where the removal of such devices would interrupt the continuity.

[This message has been edited by Larry Fine (edited 08-18-2006).]