Hi I would like to know where in the NEC talks about using liquidtight conduit to connect a dry type transformer because fo vibration. Thank you
Top
2017 / 2014 NEC & Related Books and Study Guides
#99513 - 05/27/06 04:41 AM Re: liquidtight
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Welcome to the forum victor.

You will not find anything in the NEC requiring liquidtight conduit to be used to connect a dry type transformer because of vibration.

It is just a design choice buy the installer.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#99514 - 05/27/06 12:03 PM Re: liquidtight
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
I'll go a bit farther...

True, the NEC does not address the matter. However, NECA standards document the use of flex at transformers as "trade practice", or good workmanship.

That aside, I noticed recently that some transformers have internal rubber mounts, so the piping actually does not connect to the part that vibrates.

I still like to see flex at the case, though. Old habits die hard.
Top
#99515 - 05/30/06 07:40 PM Re: liquidtight
victor Offline
Junior Member
Registered: 05/27/06
Posts: 3
Loc: Las Vegas
hi thank you for your reply, where can I get a copy of NECA stating the use of liquid flex as a good workmanship. Thank you
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals