#99477 - 01/02/06 10:57 AM Dryer rec. in unfinished basement
Helicon Offline
Junior Member
Registered: 08/11/05
Posts: 4
Loc: massachusetts
most guys installing dryer/washer receptacles or even a standard 120v 15a recetacle in a basement first mount a wooden board to a cement wall... is that required by code, or is it legal to install receptacle directly to a concrete wall?
Top
2017 / 2014 NEC & Related Books and Study Guides
#99478 - 01/02/06 11:18 AM Re: Dryer rec. in unfinished basement
Celtic Offline
Member
Registered: 02/26/05
Posts: 361
Loc: NJ
It's not the outlet that is in question, it is the wiring method:
334.12 Uses Not Permitted.
(10) Types NM and NMS. Types NM and NMS cable shall not be used as follows:
d. Where exposed or subject to excessive moisture or dampness

The cement wall *can* be considered to be a "damp" location and be easily tested by taping some plastic to the wall...after a few days moisture may appear on the inside of the plastic.

I don't know about you (or anyone else), but it's a whole lot easier to just slap up a half a 2x4 up on the wall and staple the wire to it than it is to "test" the wall and strap the NM to the cement.
_________________________
~~ CELTIC ~~
...-= NJ =-...
Top
#99479 - 01/02/06 01:42 PM Re: Dryer rec. in unfinished basement
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
You can attach the receptacle to the wall.
Top
#99480 - 01/02/06 04:09 PM Re: Dryer rec. in unfinished basement
Celtic Offline
Member
Registered: 02/26/05
Posts: 361
Loc: NJ
...but not the wire.
_________________________
~~ CELTIC ~~
...-= NJ =-...
Top
#99481 - 01/03/06 05:41 AM Re: Dryer rec. in unfinished basement
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
The question did not ask about wire but if it did, I would not consider the inside of a concrete basement wall excesively damp under most conditions.

[This message has been edited by Electricmanscott (edited 01-03-2006).]
Top
#99482 - 01/12/06 05:23 PM Re: Dryer rec. in unfinished basement
Trick440 Offline
Member
Registered: 08/15/05
Posts: 247
Loc: Waterford, MI, USA
You guys just run wire down the wall?

We use this stuff called EMT works great. Throw some 10-3 down that bad boy and its done before you even find your 2x4.

[This message has been edited by Trick440 (edited 01-12-2006).]
_________________________
Shake n Bake
Top
#99483 - 01/15/06 02:22 PM Re: Dryer rec. in unfinished basement
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Using wood is the cheapest way of doing for sure, but I prefer doing it in pipe too. It looks more professional and the NM is w/o a doubt protected from physical damage. I can consider that an important thing to do, especially any receptacle operating at 220 volts in an unfinished basement!
Top
#99484 - 01/15/06 06:28 PM Re: Dryer rec. in unfinished basement
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I'm not even sure wood is the cheapest way ... if you buy the wood.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals