The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Trumpy 6
Who's Online
1 registered (brsele), 230 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#99442 - 09/07/05 03:36 PM 250.64
markp Offline
Member

Registered: 04/12/04
Posts: 60
Loc: Kent, WA, USA
Has anyone noticed the subtle deletion of "severe" from 250.64? The way I read it now, you need to protect GEC's sized 4 and larger from physical damage whereas previously it only had to be protected from severe physical damage. We may end up needing to put just about every GEC in conduit...

[This message has been edited by markp (edited 09-07-2005).]
_________________________
Mark
Kent, WA

Top
2014 / 2011 NEC & Related Books and Study Guides
#99443 - 09/07/05 03:38 PM Re: 250.64
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Thats a great catch! Nicely done!
_________________________
Ryan Jackson,
Salt Lake City

Top
#99444 - 09/07/05 07:15 PM Re: 250.64
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
"Exposed to physical damage" is always going to be a judgement call. This change has certainly tossed some mud in the water. Basically if you can't run the #4 without a raceway, you can't run it is PVC either because that says 352.10(F) Exposed. For exposed work where not subject to physical damage if identified for such use"
_________________________
Greg Fretwell

Top
#99445 - 11/04/05 10:05 AM Re: 250.64
Helectric Offline
Member

Registered: 01/07/05
Posts: 91
Loc: Brandon, SD
And yet 250-64(b) seems to imply that a #6 or smaller can be protected with PVC if exposed to physical damage.

Top
#99446 - 11/04/05 12:13 PM Re: 250.64
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
Someone explain to me how a GEC Indoors, behind a transformer, going up a wall, would be exposed to physical damage?

Or for that matter, how does a GEC originating in a panel, going up to building steel, get damaged?

Dnk...

Top
#99447 - 11/04/05 01:57 PM Re: 250.64
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Dnk, I think we all agree there are places where a wiring method is not subject to any physical damage. This question pertains to the difference between severe physical damage and physical damage.
This is just going to be a judgement call.
_________________________
Greg Fretwell

Top
#99448 - 11/04/05 02:16 PM Re: 250.64
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
I know G, just curious if any one has seen this happen and how.

I can't imagine how a GEC can be damaged, other than blatant negligence.

Dnk...

Top
#99449 - 11/04/05 03:02 PM Re: 250.64
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Usually GECs get damaged by lawn mowers or other equipment running up next to the wall from what I see. I can't see a problem inside a building unless it is a shop or warehouse where there is some heavy material being stored against or moving by an unprotected run.
_________________________
Greg Fretwell

Top
#99450 - 11/05/05 10:24 PM Re: 250.64
Paulp Offline
Junior Member

Registered: 11/03/05
Posts: 7
Loc: Troutdale,Oregon,U.S
Does GEC stand for grounding equipment conductor? I am used to seing as EGC. I guess its probably which coast you live on.

Top
#99451 - 11/05/05 11:48 PM Re: 250.64
dmattox Offline
Member

Registered: 10/20/04
Posts: 267
Loc: Anaheim, CA
GEC = Grounding electrode conductor
EGC = Equipment grounding conductor

GEC is for connecting your grounding electrodes together to form your grounding electrode system.

EGC is the wire/conduit to bond equipment.

[This message has been edited by dmattox (edited 11-06-2005).]