#99442 - 09/07/05 03:36 PM 250.64
markp Offline
Member
Registered: 04/12/04
Posts: 60
Loc: Kent, WA, USA
Has anyone noticed the subtle deletion of "severe" from 250.64? The way I read it now, you need to protect GEC's sized 4 and larger from physical damage whereas previously it only had to be protected from severe physical damage. We may end up needing to put just about every GEC in conduit...

[This message has been edited by markp (edited 09-07-2005).]
_________________________
Mark
Kent, WA
Top
2017 / 2014 NEC & Related Books and Study Guides
#99443 - 09/07/05 03:38 PM Re: 250.64
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Thats a great catch! Nicely done!
_________________________
Ryan Jackson,
Salt Lake City
Top
#99444 - 09/07/05 07:15 PM Re: 250.64
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
"Exposed to physical damage" is always going to be a judgement call. This change has certainly tossed some mud in the water. Basically if you can't run the #4 without a raceway, you can't run it is PVC either because that says 352.10(F) Exposed. For exposed work where not subject to physical damage if identified for such use"
_________________________
Greg Fretwell
Top
#99445 - 11/04/05 10:05 AM Re: 250.64
Helectric Offline
Member
Registered: 01/07/05
Posts: 90
Loc: Brandon, SD
And yet 250-64(b) seems to imply that a #6 or smaller can be protected with PVC if exposed to physical damage.
Top
#99446 - 11/04/05 12:13 PM Re: 250.64
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Someone explain to me how a GEC Indoors, behind a transformer, going up a wall, would be exposed to physical damage?

Or for that matter, how does a GEC originating in a panel, going up to building steel, get damaged?

Dnk...
Top
#99447 - 11/04/05 01:57 PM Re: 250.64
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Dnk, I think we all agree there are places where a wiring method is not subject to any physical damage. This question pertains to the difference between severe physical damage and <some other kind of> physical damage.
This is just going to be a judgement call.
_________________________
Greg Fretwell
Top
#99448 - 11/04/05 02:16 PM Re: 250.64
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
I know G, just curious if any one has seen this happen and how.

I can't imagine how a GEC can be damaged, other than blatant negligence.

Dnk...
Top
#99449 - 11/04/05 03:02 PM Re: 250.64
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Usually GECs get damaged by lawn mowers or other equipment running up next to the wall from what I see. I can't see a problem inside a building unless it is a shop or warehouse where there is some heavy material being stored against or moving by an unprotected run.
_________________________
Greg Fretwell
Top
#99450 - 11/05/05 10:24 PM Re: 250.64
Paulp Offline
Junior Member
Registered: 11/03/05
Posts: 7
Loc: Troutdale,Oregon,U.S
Does GEC stand for grounding equipment conductor? I am used to seing as EGC. I guess its probably which coast you live on.
Top
#99451 - 11/05/05 11:48 PM Re: 250.64
dmattox Offline
Member
Registered: 10/20/04
Posts: 265
Loc: Anaheim, CA
GEC = Grounding electrode conductor
EGC = Equipment grounding conductor

GEC is for connecting your grounding electrodes together to form your grounding electrode system.

EGC is the wire/conduit to bond equipment.

[This message has been edited by dmattox (edited 11-06-2005).]
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals