#99425 - 11/02/05 06:05 PM 215.4B
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
This isn't new to 05 but here's the question:
As we read this it disallows a paralleled feeder to a sub panel (from a main dist panel) if the sets are in 2 or 3 pipes (one set per pipe). We have many panels fed by two EMT pipes that originate at a breaker in a dist panel, where each contains all the phases, a neutral and a grond. We're obviously missing something here. Maybe we aren't defining "common neutral" properly. Or maybe we have a lot of illegal panels.
Your input is appreciated.
Top
2017 / 2014 NEC & Related Books and Study Guides
#99426 - 11/02/05 08:45 PM Re: 215.4B
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
The reference to common neutral means you are only running one neutral back to the panel for multiple parallel phase sets. If you pull a neutral with each set you can split them up in separate raceways.
It is just an inductive heating problem because all neutral current would be in one pipe with the outgoing current split up among the others.
_________________________
Greg Fretwell
Top
#99427 - 11/03/05 03:22 AM Re: 215.4B
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
We follow that but here's what threw us: look at the cut & paste from the code ... what does the NEC mean by "ALL conductors of ALL feeders". Doesn't that seem to indicate every individual conductor of each set? Or do they interpret each set as a separate feeder? Or, again, are we just interpreting it wrong?

"Where installed in a metal raceway or other metal enclosure, all conductors of all feeders using a common neutral shall be enclosed within the same raceway or other enclosure as required in 300.20."
Top
#99428 - 11/03/05 04:27 AM Re: 215.4B
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Steve,
If you have a grounded conductor in each raceway, you don't have a common neutral and the section that you cited does not apply. The section for your installation is 310.4.
Don
_________________________
Don(resqcapt19)
Top
#99429 - 11/03/05 02:51 PM Re: 215.4B
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
I see we were just interpereting "common neutral" wrong. Thanks for the input.
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals