The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 182 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99399 - 06/28/05 04:10 AM Does this fitting show marking with that information?
Joe Tedesco Offline

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
With any splices in this fitting, assume 14 AWG's, we would need a box with at least 10 cubic inches [5 x 2 CU IN].

Does this fitting show marking with that information?

I posted this because this transition seems to require only wiring methods that include an EGC, such as MC and NM.

What do you say?
Joe Tedesco, NEC Consultant

2014 / 2011 NEC & Related Books and Study Guides
#99400 - 06/28/05 08:16 AM Re: Does this fitting show marking with that information?
gfretwell Offline


Registered: 07/20/04
Posts: 9023
Loc: Estero,Fl,usa
There is also a fitting for AC cable (wiremold 5790B) but the instructions seem to imply that you use a "short section of raceway to the fitting" (from a box where the splice would be made?). I agree it is hard to find anything firm about how these are installed in the PDFs I have looked at.
I'm sure a careful installer could stuff 2 wirenuts in this "mouse" but I agree it is a violation of the box fill rule.
Greg Fretwell

#99401 - 06/28/05 12:22 PM Re: Does this fitting show marking with that information?
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I believe it is improper to apply the box fill rule here....assuming the component is part of a listed system. As such, a determination was made that there was adequate space.
A similar situation occurs with every bath fan...the wiring space is a lot less than your usual box.

I actually think that these things are treated a 'appliances,' as their application is so narrow.

FWIW, I think you'll find the elbows in these systems are also somewhat tighter than we are allowed to make. And I defy anyone to pull wire through a 'completed raceway' of this have to piece it together as you go.

#99402 - 07/22/05 02:13 PM Re: Does this fitting show marking with that information?
hbiss Offline

Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
Don't know where that illustration came from. Obviously it's wrong.

You would not make a splice in that transition nor would you bond the ground as shown. The conductors should continue through to the first box.

This is no different than a transition fitting to EMT from AC, MC or NM.


#99403 - 08/19/05 12:54 PM Re: Does this fitting show marking with that information?
earlydean Offline

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Check out this cut-sheet:

You have to buy all the fittings to connect the wires and the ground. Only then is it a UL assembly.

#99404 - 10/02/05 08:24 PM Re: Does this fitting show marking with that information?
AllClear Offline

Registered: 08/22/05
Posts: 39
Loc: Belmond Iowa US
110.3 (B) Installation and use.
Listed or labeled equipment shall be installed and used in accordance with Any Instructions included in the Listing Or Labeling.

If Wiremold Instructions or Pic's tell you to do it that way then go ahead.
It's Not The Fall That Kills You...
It's That Sudden Stop At The End