The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 78 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#99309 - 03/13/05 06:35 PM Supplemental Electrode Needed?
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
If the metal frame of a building is bonded to the metal water pipe as allowed in 250.52(A)(2) method #2, then the metal frame is allowed to be the supplemental electrode as allowed by 250.53(D)(2)

With this scenario though, when the metal water pipe is replaced with plastic down the road, the electrode system is lost altogether.

We need to supplement this scenario with a additional electrode such as ground rods because the metal frame of the building will no longer be effectively grounded when the metal water pipe is replaced with non-metalic pipe.

shortcircuit

Top
2014 / 2011 NEC & Related Books and Study Guides
#99310 - 04/01/05 11:02 AM Re: Supplemental Electrode Needed?
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
250.52(A)(1) requires the metal underground water pipe to be in contact with the earth for 10 feet or more. As soon as you replace this pipe with non-metallic pipe, you have changed the grounding electrode system, and the GES must then be re-evaluated to meet current code. You don't get a free ride by going in through the back door.
This is why ALL work must have a permit applied for, so the inspector may determine if code compliance is achieved.
_________________________
Earl

Top
#99311 - 04/21/05 02:35 PM Re: Supplemental Electrode Needed?
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
earlydean, let's clarify your post.

250.52(A)(1) states that IF a metal water pipe IS to be used as a grounding electrode, it must be in contact with the earth for 10 feet or more.

250.52 doesn't state that a water pipe MUST be used as an grounding electrode.

EX. well water systems, plastic pipe incoming water.

However, if it is used as a grounding electrode and meets the earth contact requirement,it MUST be supplemented.

Does anyone else read it this way, or is it just me?

Dnk...

Top
#99312 - 04/21/05 04:53 PM Re: Supplemental Electrode Needed?
clearyjr Offline
Junior Member

Registered: 03/05/05
Posts: 3
Loc: new windsor, NY USA
250.53(D)(2) Supplemental electrode required. Generally we look for 25 ohms or less of earth ground with one rod and water main, so if this is not achived then we install another rod etc.....
So metal water main or not 25ohms or better should be the rule.